For a 30 amp branch circuit for field installed skeleton neon tubing installed using PVC conduit, what is the minimum size copper equipment grounding conductor required for grounding metal parts?

Prepare for the Electrical Code 3 Exam. Practice with flashcards and multiple-choice questions, each with hints and explanations. Get ready and pass your exam!

Multiple Choice

For a 30 amp branch circuit for field installed skeleton neon tubing installed using PVC conduit, what is the minimum size copper equipment grounding conductor required for grounding metal parts?

Explanation:
Grounding conductors are sized based on the overcurrent device protecting the circuit, so they provide a low-impedance path for fault current to trip the breaker. For a 30-amp branch circuit, the NEC table for equipment grounding conductor sizing requires a 10 AWG copper conductor. In this setup, the skeleton neon tubing is installed in PVC conduit, which does not provide a grounding path by itself, so you must run a separate copper equipment grounding conductor with the circuit to ground the metal parts. The metal parts must be bonded to this conductor so that a fault current has a proper path to trip the breaker quickly. The other sizes aren’t correct: 8 AWG is larger than necessary; 12 AWG and 14 AWG are too small for a 30-amp circuit and wouldn’t meet the required grounding conductor size. Hence, the minimum required is 10 AWG copper.

Grounding conductors are sized based on the overcurrent device protecting the circuit, so they provide a low-impedance path for fault current to trip the breaker. For a 30-amp branch circuit, the NEC table for equipment grounding conductor sizing requires a 10 AWG copper conductor.

In this setup, the skeleton neon tubing is installed in PVC conduit, which does not provide a grounding path by itself, so you must run a separate copper equipment grounding conductor with the circuit to ground the metal parts. The metal parts must be bonded to this conductor so that a fault current has a proper path to trip the breaker quickly.

The other sizes aren’t correct: 8 AWG is larger than necessary; 12 AWG and 14 AWG are too small for a 30-amp circuit and wouldn’t meet the required grounding conductor size. Hence, the minimum required is 10 AWG copper.